AgTalk Home
AgTalk Home
Search Forums | Classifieds (78) | Skins | Language
You are logged in as a guest. ( logon | register )

Outdoor wood stove, boiler versus forced air.
View previous thread :: View next thread
   Forums List -> AgTalk CafeMessage format
 
PaKettle
Posted 4/3/2020 08:27 (#8160377 - in reply to #8160315)
Subject: RE: Outdoor wood stove, boiler versus forced air.



Lenawee Co Michigan
With a floor heat boiler for your shop or house, you would need antifreeze in the water so it didn't all freeze up and break if power went out or nobody around to fire the boiler. You really can't tap this hot coolant out for other uses if it's ant-freeze.
Top of the page Bottom of the page


Jump to forum :
Search this forum
Printer friendly version
E-mail a link to this thread

(Delete cookies)