Am I going to fail my MN State electrical inspection? Pics
View previous thread :: View next thread
   Forums List -> Kitchen TableMessage format
 
45Deere9670
Posted 6/6/2020 14:14 (#8301451 - in reply to #8299989)
Subject: RE: Am I going to fail my MN State electrical inspection? Pics


St. Joseph, Champaign County, IL
Here, it’d not pass. Too many conductors in too long a run of conduit, so the amperage ratings of the conductors would have to be derated.

Since the conduit is over 24” in length, ampacity needs to be adjusted. I count 8 total NM cables, each with 2 current carrying conductors. With 16 current carrying conductors, the ampacity allowed for the #12 conductors (circuits) would be 15A. The #14 circuits would be allowed a max of 12.5A.

Edit: I have seen installs like this be passed, however.

Inspector could also want a bushing on both ends of the conduit, if doesn’t otherwise have an issue with the install.

Edited by 45Deere9670 6/6/2020 14:16