| What year of machine is this? Different years have a different Ag Leader control system on there.
If the pressure spikes when the sections turn off, it is more than likely a setting that needs to be adjusted. I would say it's the PWM standby and that would need to be lowered.
With the min flow setting, take the nozzle that you are using and find the lowest pressure they have listed for the nozzle, and find the flow rate of the nozzle at that pressure. Take the flow rate and multiply that times the number of nozzles you have and that will be the min setting. The system should not go below that value. | |
|