pfortfarm - 5/24/2020 12:38 Tedbear, thank you very much for that excellent explanation. So, everything seems to be communicating like it should. Discovered I had two Solenoids that were bad so swapped them out with some spares in the box of stuff that came with the system and now it is working according to the switches. Biggest issue I have now is that the solenoids get really hot. According to their diagram, they have each solenoid neutral coming to a common stud and that is grounded to the Slectro framework, which the solenoids are fastened to as well. They are metal construction. Check to see that the arms are installed the proper way. They can be upside down and still work, but will pull to many amps and pop the breaker after a bit. I had one that was upside down, changed it to the correct position and all was well. |