Winkler, Manitoba Canada | Angus8335 - 3/19/2025 20:23
Motor tag says 28 amps 230 volts 3ph. That should = 6440 watts.
Your power calculation forgot to compensate for 3 phase power. Multiply your answer by 1.732 to get closer to a correct answer. Really need to compensate for power factor as well, but that is a smaller factor.
https://learnmetrics.com/3-phase-power-calculator-formula/
If you have single phase power available a vfd could be employed to run the 3 phase motor. I do not think it is practical to do what you are suggesting otherwise.
The timing and interval of your proposal suggests you are pumping water. I believe the companies who provide a solar solution to do that use DC pumps that will run at varying speeds depending on the power available. An AC motor will not function well under that scenario. |