230 v starter relay
View previous thread :: View next thread
   Forums List -> Where Can I find?????Message format
 
tj_farms
Posted 1/23/2019 20:45 (#7267565 - in reply to #7267399)
Subject: RE: 230 v starter relay



Ohio
clayball farms - 1/23/2019 19:55

I need a way to start and stop a 10 hp, 1phase motor from a distance. The motor powers a grain transfer auger between bins. I would prefer running power from main power supply directly to motor. However, the logical place to start and stop auger is 100-120 ft away. Is there a simple relay/ starting switch that can start and stop motor.? It could be powered by a small switch and light ga. wire , rather than running heavy ga. supply wire all the way to switch and back to motor. Any sugestions ?? TIA


Do you have a contactor wired in the circuit to motor now ? If not you will need a motor starter wired to the motor and then you can wire a remote switch to it as far as you want away, only need 10-16 gauge wire for the remote switch. Here is some reading about it.

https://www.google.com/search?source=hp&ei=ZCVJXOT0Oc-J5wLozJ9A&q=mo...

Here's something like you need, 10 1PH requires a 50-65 amp starter or bigger.

https://www.ebay.com/itm/Elimia-Air-Compressor-Pump-Motor-Starter-23...

And some directions for the remote switch.

https://www.springercontrols.com/news/single-phase-motor-3-phase-con...




.

Edited by tj_farms 1/24/2019 09:36