WTW
Posted 3/28/2025 09:15 (#11164937 - in reply to #11164867)
Subject: RE: 220 volt 3 wire question


Winkler, Manitoba Canada
ccjersey - 3/28/2025 07:28

Yes, if you’re using this generator for backing up
a normal mix of loads that includes lots of 120 volt circuits IN A PANEL THATS NORMALLY SUPPLIED BY THE UTILITY, you want the neutral to be the same size as the lines. Ground can normally be smaller.



Pretty sure all of 120/240 volt single phase distribution on the yard, whether that be utility or privately supplied, has a reduced neutral. Neutral only carries the unbalanced load.