Butterfield, MN | That cable isn't going to do the trick. The only one I know of is a 115-0172-054. Other than also providing a speed output, the only real difference I know of compared to most of the other cables is that it contains a cross-over or jumper inside, which is required to make a SCS console communicate with the Cruizer II for some reason. I'm not sure why this was necessary, as other monitors from Raven only require a null modem cable, but that's going to be a big reason why the two will not communicate. This cable would connect to port A, port A baud in the Cruizer II would need to be set to 9600, port setup in the 450 would also need to be set to 9600. I haven't tried it without doing it this way, so I would also set the trigger value to 1, trigger units to seconds and turn data logging on. It may not require it, but I always set these things up the same. | |
|